Indoor Air Quality
If the optional indoor air quality sensor is installed, the
RTU --MP will maintain indoor air quality within the space
at the user configured differential setpoint. The setpoint is
the difference between the indoor air quality and an
optional outdoor air quality sensor. If t he outdoor air
quality is not present then a fixed value of 400ppm is
used. The following conditions must be true in order for
this algorithm to run:
S The mode is occupied.
S Indoor Fan has been ON for at least 30 seconds.
S Indoor Air Quality sensor has a valid reading
As air quality within the space changes, the minimum
position of the economizer damper will be changed thus
allowing more or less outdoor air int o the spac e depe nding
on the relationship of the indoor air quality to the
differential setpoint. If all the above conditions are t rue,
the IAQ algorithm will run and calculates an IAQ
minimum position value using a PID loop. The IAQ
minimum damper position is then compared against the
user configured economizer minimum position and the
greatest value becomes the final minimum damper
position of the economizer output.
If the calculated IAQ minimum position is greater than
the IAQ maximum damper position configuration then it
will be clamped to the configured value.
Demand
Limit
If the RTU --MP receives a level 1 (one degree offset), 2
(two degree offset), or a 3 (4 degree offset) to the BACnet
demand limit variable, the controller will expand the
heat ing and cooling setpoints by the configured dem and
limit setpoint value and remain in effect until the BACnet
demand limit variable receives a 0 value.
FASTENER TORQUE VALUES
See Table 25 for torque values.
Table 25 Torque Values
Supply fan motor mounting
120 ¦ 12 in ---lbs 13.5 ¦ 1.4 Nm
Supply fan motor adjustment plate
120 ¦ 12 in ---lbs 13.5 ¦ 1.4 Nm
Motor pulley setscrew
72 ¦ 5 i n --- l b s 8.1 ¦ 0.6 Nm
Fan pulley setscrew
72 ¦ 5 i n --- l b s 8.1 ¦ 0.6 Nm
Blower wheel hub setscrew
72 ¦ 5 i n --- l b s 8.1 ¦ 0.6 Nm
Bearing locking collar setscrew 65 to 70 in ---lbs 7.3 to 7.9 Nm
Compressor mounting bolts 65 to 75 in---lbs 7.3 to 7.9 Nm
Condenser fan motor mounting bolts
20 ¦ 2 i n --- l b s 2.3 ¦ 0.2 Nm
Condense r fan hub setscrew
84 ¦ 1 2 i n --- l b s 9.5 ¦ 1.4 Nm
580J